Issue

Receive data from Trend log (Seven Trends) with incorrect base time hh:12 even though it is set to 00:00.  

Environment

I/NET Seven 

Seven Trends

Xenta Server 527 / 527-NPR / 731

Cause

When using a Xenta Server as an I/NET NetPlus Router (NPR) and have configured a Trend (Seven Trends) with a sample count of 24 and sample interval of 60 minutes it appears that the time is incorrectly reported to the I/NET Host.  This issue will be rectified in a future release of the Xenta Server firmware. 

Resolution

As workaround to this issue, the Sample Count value below 24 should be used.  

This is issue is not seen when using a Direct Connect configuration 