Sharing a CO2 sensor between Xenta 102-AX controllers

Issue

Several Xenta 102-AX controllers need to have the CO2 sensor shared among them in a LNS environment.

Environment

  • CO2 (Carbon Dioxide)
  • Xenta 102-AX
  • nviCO2
  • nvoCO2sensor

Cause

Properly binding a CO2 sensor output to multiple Xenta 102-AX VAVs.

Resolution

From the Xenta 102-AX VAV that is connected to the CO2 sensor, create a binding from the UnivIn3Sense function block/nvoCO2sensor, to VAV_Controller function block/nviCO2 in the receiving Xenta 102-AX VAVs.

It will also be necessary to set the send heart beats by following Lesson Learned Article #4002.