Sigma - Integrated Controller (IC-Lon), objects show default values.

Issue

IC-Lon objects show default values.

Environment

IC-Lon

Defaults

Default values

Sleep

Cause

The IC-Lon controller works normally for a varying period of time, before default values are displayed.

Resolution

The IC-Lon has a number of limitations, and one of these is the number of output SNVT's used, and the frequency of the heartbeats used.

When configuring the gateway.txt file for the IC-Lon ensure that all NVO's have their heartbeat settings set to an acceptable maximum value, and that the settings used vary.

By default the NVO 's heartbeat value is set to 300 seconds, these should be changed to the acceptable maximum