Sigma - Releases 4.05 SEB or 4.06 when used with the Remote Alarm Manager.

Issue

Sigma configurable Data location.

Environment

Sigma 4.05 SEB

Sigma 4.06

RAM

Remote Alarm Manager

1.2

2.0

Data location

Cause

Although Sigma 4.05 SEB and 4.06 support a configurable Data location, RAM does not.

Resolution

When using the Remote Alarm Manager version 1.2 with Sigma 4.05 SEB, the Sigma Data location must not be changed from the default of C:\Sigma\, as this is not supported by RAM version 1.2.

Please note that the release note suggests that a "Compatible" version will be available, this is not the case.

When using the Remote Alarm Manager version 2.0 with Sigma 4.06, the Sigma Data location must not be changed from the default of C:\Sigma\, as this is not supported by RAM version 2.0.

To access the release notes for the releases mentioned above, please visit the Schneider Electric's Exchange/Download Center.