SmartStruxure BACnet Default Priority Level.

Issue

Is there a way to specify the priority that the system should use by default when writing to the value of BACnet objects?

Environment

Enterprise Server - ES

Automation Server - AS

WorkStation

Cause

Documentation

Resolution

In order to allow users to specify the default priority used when writing to the VALUE property of BACnet objects a property has been added to the Interface Manager as seen in the screen shot below.

Note that you can still write at other priorities by binding directly to the desired priority.



The default priority level DOES NOT apply to processes that contain their own internal priority such as Schedules and Loops.

Also, Script programs created in a b3 do not follow the default priority level (they still use priority 10)