Some of the dynamic values on a graphic screen in InVue are not updating.

Issue

Each time an InVue graphic screen appears, not all of the dynamic values (tags or remote references) update. 

No error messages appear.

Environment

InVue 1.1

WIBS 1.1

Wonderware

Cause

The InVue computer hardware was replaced. 

It has a dual/multi-core CPU which was never validated with InVue.

Resolution

Disable the settings in the computer's BIOS such that the CPU behaves like it is a single-core.