Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

StruxureWare Building Operation 1.3/1.3 SP1 reports "The upper limit must be greater than or equal to the lower limit and indicates the import is complete".

Issue

Importing a VisiSat pointslist StruxureWare reports a limit issue and suggests the import is complete.

Environment

StruxureWare Building Operation 1.3/1.3 SP1

Cause

On one of the VisiSat points being import,  the alarm limits have been incorrectly set.


 

Although StruxureWare Building Operation 1.3/1.3 SP1 reports that the import completed in X minutes and X second, the import would have failed to complete due to the stated issue.
Unfortunately the reported limit issue can effect 100 points or just the 1 point. 
The specific point or points identity is not highlighted in the trace file.
 

Resolution

Locate the point and check the alarm limits are entered correctly. The example below show the upper limit and lower limit are reversed.

Change it so the upper limit is above the lower limit.

Tags (1)
Version history
Revision #:
2 of 2
Last update:
a week ago
Updated by:
 
Contributors