Issue

Binding a PVR module in the Function Block Program directly to a "Value" object?

Environment

Function Block Program

FBP

PVR module

Cause

The PVR module is not available to bind in the binding window.

Resolution

To enable the PVR module to be bound, it must first be made "Public", this is selected when editing the module.

 

 

Having saved the Function Block Program, the PVR module can now be bound in the normal way.

 