TAC Menta, mainloop overrun then having many Alarm blocks and more than one ERR block.

Issue

TAC Menta could give mainloop overrun then having an application with many Alarm blocks and more than one ERR block.

Environment

TAC Xenta 280/300/401
TAC Menta

Cause

When the ERR block is executed, it goes through all Alarm blocks to check status, having more than one ERR block makes this loop to be run more than once.

Resolution

There sould be a maximum of one ERR block per application.