The BDelay object from the LonWorks jar conversion library intermittently shows very large "remaining time" causing logic issues.

Issue

The BDelay object from the LonWorks jar conversion library intermittently shows very large "remaining time" causing logic issues.

Environment

R2, UNC's

Cause

The BDelay object does not initialize the time remaining properly under some conditions.

Resolution

In the Lib jar - programObjects - hvac folder there is a program called DelayedOutput.sns.  This program can do the delayed on and off function but will need to be enhanced if the time remaining output is required.