Issue

The Function Block in LonMaker has a completely different set of SNVTs than the associated MTA file.

Environment

  • LonMaker
  • Menta

Cause

It is possible to have 2 completely different TAC Xenta (300/400/280) controllers that have the same program ID. LonMaker will use the same template for all devices with the same program ID. To fix this you have to get a new program ID for one of the controllers.

Resolution

Follow the steps below to get a new program ID for your controller:

  1. Open the application from System plug-in by right clicking on controller and select configure-edit.
  2. To give the application a new XIF either add a “dummy” SNVT or go to device configuration and uncheck the tick box for “XIF header generated according to LonMark standard”.
  3. Hit F12, select commands and generate. Hit F12 again and save the application to the hard drive by selecting File-save as.
  4. In system plug-in, browse in the application that you just saved on the hard drive. Update TAC Network and TAC Database. If you are asked to resynchronize, do so.
  5. Download application and parameters to the controller.