Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

The I/A Series R2 (Niagara) build 529 programLib jar file is missing 5 objects that were available in a previous build.

Issue

The I/A Series R2 (Niagara) build 529 programLib jar file is missing 5 objects that were available in
previous build programLib-2.301.527c.v1.jar.

The missing objects include:

  1. ConfigurableBinaryOutputNode.class
  2. FlexLimitEnableBits.class
  3. FlexString.class
  4. Bpa2Str.class
  5. Fs2Fp.class

Environment

I/A Series R2 (Niagara) build programLib-2.301.529.v1.jar

Cause

Objects listed were not included in programLib-2.301.529.v1.jar

Resolution

The missing objects were restored in the programLib-2.301.532d.jar. Use it instead of the programLib-2.301.529.v1.jar.

  1. In Windows Explorer, rename programLib-2.301.529.v1.jar. to programLib-2.301.529.v1.jar.old in the emb, nre/modules, and nt directories.
  2. Download programLib-2.301.532d.jar
  3. Copy into all three 2.301.529.v1 directories (emb, nre/modules, and nt ).
Tags (1)
Labels (1)
Version history
Revision #:
2 of 2
Last update:
‎2018-09-07 10:09 PM
Updated by:
 
Contributors