The ProView for LON Display shows the enumeration definitions for SNVT_tod_event even though the wizard is set up to use SNVT types with different enumerations.

Issue

The ProView for LON Display shows the enumeration definitions for SNVT_tod_event even though the wizard is set up to use SNVT types with different enumerations.

Environment

Niagara R2 & G3

Proview

Cause

Display conflict

Resolution

Although the schedule does not display the desired enumerations, the schedule's "value" is successfully sent to the bound controller. This issue has been observed on both Niagara R2 and G3 platforms. It applies to version 2.62 of the ProView display. Distech Controls, the makers of the display, have been informed of this "display-only" issue. For now, OCCUPIED and UNOCCUPIED are the enumerations that will work.