The damper position is sometimes displaying a value of "NA"?

Issue

The damper position is sometimes displaying a value of "NA"?

Environment

MNB-V1 and MNB-V2

Cause

The VAVActuator object in the controllers database has its position initialization mode set to 0 which means it will initialize the position value at its earliest opportunity following a reset. Therefore, the position will display as NA until the controller hits one stop or the other.

Resolution

The VAVActuator object in the controllers database has three options for the position initialization mode following a reset.  If having the position display NA for a time following a reset is not desirable the position initialization mode can be set to force the controller to go open or closed following a reset and then it will display a value for the position following a reset.