This alarm is trigged every day "trendlog object...log point can not be read" how do I get rid of it?

Issue

This alarm is trigged every day "trendlog object...log point can not be read" how do I get rid of it?
The trendlog is a Vista server trendlog logging a point in a Xenta 400

Environment

Vista 5.1.6

Cause

When a Vista server trendlog is started Vista reads the chosen value according to the log interval, if one reading is missed you will see this alarm.
The missed reading could have several reasons but the most common is a bad Lon network or high traffic on the Lon network. 

Resolution

Investigate why the logged value can't be read, check the Lon network with a analyzer.
 