Time Zone and DST when syncing time to an NTP server.

Issue

  • Time Zone and DST when syncing time to an NTP server
  • Time differs from NTP server with x hours.
  • DST is not following NTP server time.

Environment

TAC Xenta 701, TAC Xenta 711, TAC Xenta 731,TAC Xenta721, TAC Xenta 511, TAC Xenta 527

NTP server

Cause

NTP provides UTC, no information about time zones or daylight savings ( DST)  is sent. So if you don't set the correct time Zone and DT settings the time will be set to UTC time in the device.

Resolution

Log in to Xenta server

Go to  Configuration- Time- Regional Settings

Set correct information