Transfer SNVT (network variables) between lon devices in a TAC Vista Classic scenario

Issue

Transfer SNVT (network variables) between lon devices in a TAC Vista Classic scenario.

Can't bind in classic network; how to send SNVTs from one lon device to another?

Environment

TAC Vista Classic scenario LonWorks devices

Cause

If you are using TAC Vista in a classic scenario, no real SNVT bindings can be made.

Resolution

Use object transfer to send the values. Note that the server have to be running for the values to be transferred.

For more info on how to set up object transfer, see Chapter 14 in the TAC Vista Technical Manual.