Issue

No Trends are showing up in the Data/Enquiry Editor when a point is selected.

Environment

Xenta 527-NPR and Webserver 5.1.6

Cause

Changes in the Xenta 527 firmware in version 5.1.6 and later have resulted in some problems I/NET trend data displaying in the Xenta 527-NPR.

Resolution

To resolve this, the best option is to downgrade the Xenta 527 to version 5.1.5, per Lessons Learned Article #4007 and restart the device and I/NET again.