Issue

UI-8-10 module is reporting no change of state on inputs when shorted.

Environment

UI-8-10

Cause

Setting the voltage range switch to 10V when the Reference Resistor is in the on position is an invalid configuration.

Resolution

Change the voltage range settings to 5v on the input.