Unable to assign point channel due to Infinity Controller Error.

Issue

An attempt to assign an IO channel results is Infinity Controller Error - Invalid Channel Number.

Environment

CyberStation

All CXs, I2s and B3s

Cause

The OMS database in the controller does not match the sql database seen from CyberStation.

This can occur if the controller has re-started with a stale oms database in flash.

Resolution

Perform a Send to Controller from CyberStation to sync up the database in the controller, once all is working and the configuration is as desired perform a backup to flash of the controller.