Unable to transfer values from third party device in a Cyberstation Program.

Issue

A Cyberstation program will not transfer the value of an AnalogValue in a third party device to an AnalogValue point in Continuum.

The Cyberstation program consistently errors out and disables.

Environment

  • Point Transfer
  • BACnet

Cause

Using a Cyberstation program to set the value of a point in a BCX controller to equal the value of a point in a third party device without an intermediate step.

Resolution

  1. Create AnalogValues in the Cyberstation. 
  2. Point values should first be transferred from the third party device to the Cyberstation points.