Unable to update Vista database

Issue

Cannot update the Vista database using the Vista system plug-in when importing a Menta file.
 

Environment

  • Vista 5.1.4
  • Xenta Programmable Controllers
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • Windows 2003 Server

Cause

The object name for the "alarm control" object was misspelled in the Menta alarm block.
 

Resolution

The object name for "alarm control" must match the alarm control object name in the HMI. *In the example below the spelling is correct in both places.

Download images for better review: ALM_Block and NMI_Name

Tags (1)