Upgraded to 4.4.0 but don't see the SCPTs on a LonWorks Unit yet?

Issue

Upgraded to 4.4.0 but don't see the SCPTs on a LonWorks Unit yet?

Environment

  • Vista 4.4.0
  • Lonworks units

Cause

When you upgrade your Vista database, it doesn't automatically create new database objects. 

Resolution

  1. From Vista Workstation, navigate to a LonWorks unit
  2. Right click and select Properties.
  3. Click on the "Xif file" tab
  4. Click on the browse button (the one next to the "source file" field with 2 dots on it).
  5. Browse to the xif file for that unit, e.g. C:\lonworks\import\tac\x100\102AX101.XIF for an Xenta 102-AX
  6. Click "Open" then "OK"

When you refresh that unit in the tree, you'll see the available objects/function blocks for that unit and they will contain most of the SNVTs, SCPTs and UCPTs in them.

Some of them will not show up, e.g. ucpt_vavselection in the 102-AX.