Using an Area control in pinpoint to activate an area into a lockdown state

Issue

Clicking an Area control in pinpoint will only put the area into a lockdown state instead of cycling its lockdown state

Environment

Cyberstation

Pinpoint (Graphic)

Cause

The Area control on a graphic panel will only activate the lockdown.

Resolution

In order to remove a lockdown activation that was selected by an area control on a graphic, editing of the area object itself will need to be performed in order to remove the lockdown. This is as designed since for a security feature of locking down entire areas, there should be no mistake of double clicking on the graphics area control to accidently disable the lockdown.