Issue

Getting an error when trying to launch Run_RunBioAdmin.

Unhandled exception has occurred in your application. If you click Continue, the application will ignore and attempt to continue. I you click quit the application will close immediately. 

InvalidArgument=Value of '255' is not valid for 'SelectedIndex'.

 Parameter name: SelectedIndex.

Environment

Continuum 1.94 and above.

Cause

The database got corrupted and needed to be cleared out and restarted.

Resolution

To resolve this the following steps need to be done:

  1. Open up SQL
  2. Connect to the db and then Continuumdb
  3. Open up the Tables and expand it
  4. Look for VStationSysConfig
  5. Run a query to delete the rows in it and then restart VStation again.