Veris temperature transmitter - control system is reading an inaccurate temperature reading

Issue

Veris temperature transmitter - control system is reading an inaccurate temperature reading

Environment

Veris temperature sensor with voltage transmitter output

Cause

The Veris sensor and the controller are located at different locations and using a different common as they are being powered by different power sources. 

Resolution

Refer to the sensor's installation instructions and ensure that the sensor and controller uses the same common. 