Vista Server trend logs, logging BACnet, M-bus or modbus values, are not updating

Issue

  • Vista Server trends, logging BACnet, M-bus or modbus values, are not updating.
  • The same value being logged over and over.

Environment

TAC Vista

Xenta 700

TAC Xenta 913

Cause

This is due to a bug in the Xenta Server firmware, and happens if you have a menta application that uses other modbus values than the ones being logged.
If you open a graphic or the value columns the log works.
 

Resolution

This issue will be fixed in 5.1.9.

5.1.8 hotfixes for Xenta 913 and Xenta 700 are available on request from PSS.