Were can I find a list of object status numbers and descriptions

Issue

Were can I find a list of object status numbers and descriptions

Were can I find a list of model numbers

Environment

Continuum

Cause

Were can I find a list of object status numbers and descriptions

Resolution

1. See file Stsvc.txt in the Continuum directory

2. In Continuum Versions 1.5 and higher, a new database attribute exists.
This new attribute is "ObjectStatus".
When an objects value in the continuum system is greater than zero, then an indicator icon is placed on that object in the explorer view.
This indicator icon is also placed on the parent object and subsequent parent objects as applicable.
This indicator icon is sometimes referred to as a "bang".
This indicator icon will reveal the reason it has been placed on the object when you place your mouse over the indicator icon.
This ObjectStatus attribute value is a bit wise type of attribute.

ObjectStatus values and their descriptions:
0   - No mouse over, display normal
1   - Requires a Save from Controller (Parent)
2   - Requires a Save from Controller (Child)
4   - Requires a Flash Backup
8   - Object must be reloaded
16  - Object has been off-line edited
32  - Object has been off line created
64  - Flash backup disabled
128 - OS update fail

Combination values will display more than one description.  For example, 144 would display OS Update Fail and Object Has Been Offline Edited