What is the default Device ID / Device Instance of SE7000 series BACnet controllers.

Issue

Without knowing the Device ID / Device Instance these devices cannot add to the MSTP network in the AS or ES.

Environment

Automation Server

Enterprise Server

BACnet

SE7000

Cause

Only the MAC ID / Com Address is shown in the display but not the Device ID / Device Instance.

Resolution

SE7200x Models

Default Device ID is set to: 72000 + MAC

  • Where MAC is the current MAC address of the device.

The device ID will also be upgraded as soon as there is a change to the device’s MAC.

For example, when a SE7200F5045B controller with a MAC address of 41 is connected to a network, its default Device Name will be SE7200F5x45B-41 and its default Device ID will be 72041.

SE73xxx Models

Default Device ID is set to: 73000 + MAC

  • Where MAC is the current MAC address of the device.

The device ID will also be upgraded as soon as there is a change to the device’s MAC.

For example, when a SE7300C5045B controller with a MAC address of 63 is connected to a network, its default Device Name will be SE7300C5x45B-63 and its default Device ID will be 73063.

Integration Manual Click here.

Please refer to the Lessons Learned Article# 13125 if SE7300 controller does not come online.