What is the default IP address for a UNC, ENC, or Jace 8000?

Issue

Documentation supplied with new UNC, ENC, or Jace 8000 was discarded.  Is there a way to determine the default, factory defined IP address for the Ethernet port on the controller?

Environment

I/A Series (Niagara) R2 UNC

I/A Series (Niagara) G3 ENC

Niagara N4 or G3 Jace 8000

Cause

Lost or discarded document, shipped with controller, that contained the configured IP address.

Resolution

The default Ethernet IP address for an I/A Series (Niagara) UNC or ENC is based on the serial number and type of device.

For a UNC or ENC the default address is 192.168.1.14X where X is the last digit of the device serial number.  The default serial number is found on a sticker on the controller circuit board.  This sticker has the full model number, date code and serial number of the controller.  The serial number is preceded with S/N:.
The subnet mask is 255.255.255.0 in all UNCs, ENCs and Jace 8000

The default address base address (192.168.1.140) is the same for all UNC-410, UNC-510, UNC-520, ENC-410 and ENC-520 controllers.

The default IP address a Jace 8000 for PRI (LAN1) is 192.168.1.140.  SEC (LAN2) is by default disabled.