When attempting to create OP Trees for Xenta controllers, some public signals in the application do not appear in the OP/32 Configuration Tool.

Issue

When attempting to create OP Trees for Xenta controllers, some public signals in the application do not appear in the OP/32 Configuration Tool.

Environment

  • Xenta OP
  • OP/32 Configuration Tool

Cause

While Menta allows you to use both uppercase and lowercase module names, the OP/32 Configuration Tool is case sensitive and can only use one version of a particular module name. For example, if you refer to Air Handler 1 as both "AH1" and "ah1" modules in an application, the OP Tool will only list the points from either the capitalized module or the lowercase module; never both.

Resolution

To correct this issue and make the missing points visible in the OP Tool:

  1. Close the OP Tool
  2. Standardize the module names to the same case format
    To change module names:
    1. Select one or more blocks with the mouse
    2. When they are highlighted in green, right click and click on "Module"
    3. Type in the new module name and then click "OK".
  3. Save the application
  4. Re-open the OP Tool