Issue

When converting a station from R2 v522 to v535 getting error: "Link is not valid: Link invalid for unknown reason".

Environment

R2 UNC and WPP

Cause

The v535 LonExtras jar is not correctly handling converting  links that reference SNVT type FlexSnvtTempSetpts.

Resolution

Download and Install the v532a LonExtras jars in WPP.   Convert the station successfully then install v532a lonExtras jar and the station in the UNC.