When copying a trend log in Xbuilder 5.1.6, the green arrows on the signals disappear.

Issue

When copying a trend log in Xbuilder 5.1.6, the green arrows on the signals disappear.

Environment

TAC Xbuilder 5.1.6

Cause

Bug in the code that appeared in v5.1.6

Resolution

If you bind something to the signal or reload the project, the green arrows appears again.

This issue will be fixed in version 5.1.7.