When dragging graphic images from the Niagara G3 kitPxGraphics module, the location is wrong.

Issue

When a graphic is dragged out of the kitPxGraphics module, the image location on the px page shows ‘file:^px/’ and the path.  Sometimes the image displays, sometimes is does not display.  It behaves like this on some laptops but on others, it’s fine.

 

Environment

Niagara G3 / AX 3.8.37 server stations and soft jaces

Cause

There could be an issue with a recent Windows update.

Resolution

The work-around is to exclude a line from the system.properties file:   niagara.ui.px.maxImageModuleFileSize=2047

Place a '#' sign in front of this line and the module path is used instead of the px file space.