When logging in via WebStation the initial screen is blank

Issue

When logging in via WorkStation all is fine, but logging in via WebStation shows a blank initial screen (see below).

Environment

WebStation

Cause

The system has been configured with a user defined default workspace.

The default workspace contains an 'ampersand (&)' in the name.

Resolution

Apply hot fix 1.6.1.28100 or remove the ampersand character from the workspace's name.

NOTE: This issue exists in all versions of StruxureWare Building Operation prior to 1.8, as of the writing of this article only 1.6.1 had a hot fix available to solve the problem.

The issue has been resolved in StruxureWare Building Operation version 1.8