Why aren't the MSTP Devices coming in to SBO when upgrading site from Continuum?

Issue

Some MSTP Devices show up when learned but other are not coming in. They worked fine on the Continuum install with the same MSTP network.

Environment

Automation Server

Cause

The AS has a maximum of 50 MSTP nodes and the b3 controllers that are not coming in are above this NodeId.

Resolution

Change the b3's NodeId's to a value below 50.

1. Use the Continuum system to change the Id by deleting the device object from the database, recreating it with the new NodeId.

2. Clear the controller to factory default.