Will the TE200AD24 sensor from Greystone Energy work with a MNB controller?

Issue

Will the TE200AD24 sensor from Greystone Energy work with a MNB controller?

See the datasheet.

Environment

MNB controllers

Cause

Retrofitting an existing 3rd party control system with a MNB controller

Resolution

Any 10k thermistor Type G (U.S. Sensor), Type 9 (Dale/Vishay) or Type III (ACI Series AH) can be used with the MNL/MNB controllers.
An 11k shunt resistor wired in parallel with the sensor (1/8 watt, +/- 0.1% tolerance) is also required.
See Lessons Learned #7588.
The inputs only take a 10k resistive load.  So, for the setpoint slider, use a 10k linear pot.  The datasheet says the AP model comes with a 20-30k pot and that you’ll have to call for other values.

The 5 Vdc source required is not available on the MNB-300.  It is available on the MNB-1000