Issue

Wiring an STR-202 slide stat and override into a Xenta 102-AX

Environment

STR-202

Xenta 102-AX

Cause

The STR-202 wiring guide does not explicitly describe jumping together pins 14 and 15 of the STR and landing them both on U4 of the 102-AX.

Resolution

  1. Pins 14 and 15 of the STR-202 must be jumpered together.
  2. This output is then connected to input U4 of the 102-AX.
  3. Be sure to set the hardware configuration to "Slide Stat" in the hardware configuration tab of the 102-AX plug-in.