Issue

System error log are reporting Wm_TimeObject errors when trying to create or modify a time schedule in a Xenta server.

  • Wm_TimeObject: Http_Get Error   (Error#:41992)
  • Wm_TimeObject: Http_Post Error   (Error#:41993)
  • Wm_TimeObject: Update File Error   (Error#:41994)
     

Environment

  • Xenta Server
  • Xenta 511, 527, 711, 731
  • Time Schedules

Cause

Attempting to view or create a time schedule object page in the web browser when the time schedule resides in an offline Xenta controller.
 

Resolution

 The Xenta controller must be online to create or modify a time schedule.
 