Issue

Trying to create Modbus RTU 2nd Generation XDriver points. Filled in Xdriver tab attributes and pressed "Apply" or "OK". When refreshing or re-opening the point editor the Xdriver tab info has not saved.    

Environment

Modbus RTU Xdriver

CyberStation

Cause

The name attribute of the Xdriver comm port was changed to Modbus Comm 4 and the Alias was changed to CommX.

Resolution

  1. Change the Xdriver comm port name and alias attributes back to the default settings - in this case comm4.
  2. Points now save correctly.