Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Xenta 700 version 5.1.1 and lower, Menta TRIG block misses the triggering signal

Issue

Writing directly to DELB (delay binary) simple block in a Xenta 700 Menta application where that DELB output is sent to a TRIG block, the TRIG block may not work.

Environment

  • Xenta Servers version 5.1.1 and lower
  • Xenta 701, 711, 721, 731
  • Menta

Cause

This was a bug in version 5.1.1 and lower.

Resolution

Upgrading the Xenta Server to version 5.1.2 or later will resolve the issue.

If upgrading is not an option, this can be worked around with one of these options:

  1. Write to a block prior to the DELB block, not the DELB block itself
  2. Put a second DELB block at the end before the TRIG block
Tags (1)
Labels (1)
No ratings
Version history
Revision #:
2 of 2
Last update:
‎2018-09-09 03:29 AM
Updated by:
 
Contributors