Xenta 913 not communicating to "native" BACnet with defined Virtual Link Layers

Issue

Xenta 913 Device Template cannot map  to "native" BACnet using 485 Virtual Link Layers.

Environment

  • Xenta 913
  • BACnet

Cause

The Xenta 913 cannot connect to anything below the IP layer. "Virtual Link Layer" is not able to be used if the points are not exposed at the IP level there is not a way to address defined modules below.

Resolution

Any point that needs to be exposed at the IP level must have the ability to be mirrored in the BACnet IP device. If the IP device does not have the ability to mirror the 485 layer points, the 913 will not be able to map them.

                              Example of 485 Virtual Link Layers under BACnet IP