Issue

Xenta OP menu items: Status, Sub menu, Week chart, Holiday chart, Alarm, Access Code, Edit Access Code, Date and Time, Daylight Saving have defined Access Levels:

  • Low Level
  • Med Level
  • High Level

Accessing the medium or high level menu items requires a password. What is the default password and how can they be changed? What if the passwords have been lost?

Environment

  • Menta
  • Xenta OP

Cause

Accessing the medium or high level menu items requires a password.

Resolution

  1. Default password for accessing medium level menu items is: 1111
  2. Default password for accessing high level menu items is: 2222
  3. These can be changed via the Xenta OP only provided the "Edit Access Code" menu item is present in the OP Tree.
  4. Downloading the controller will always set the access level passwords back to the default.