Xenta Server power outage protection

Issue

  • Will the data in the Xenta Server still be intact after a power failure?
  • How long is the "power outage protection time" for the various Xenta servers?

Environment

TAC Xenta 511
TAC Xenta 527
TAC Xenta 555
TAC Xenta 701
TAC Xenta 711
TAC Xenta 721
TAC Xenta 731
TAC Xenta 911
TAC Xenta 913

Cause

Needs to know how the Xenta Server handles a power failure

Resolution

Power Outage Protection – Settings like configurations and web pages are stored in the non-volatile (flash) memory and will not be lost in the event of a power outage.
A built-in capacitor maintains operation of the RAM memory for at least 72 hours in the event of a power outage.

More information may be found in the TAC Xenta 500/700/911/913 Product Manual, chapter 2.1