Xenta server stand alone and Vista at the same time

Issue

  • Xenta server stand alone and Vista at the same time.
  • No alarms showing in TAC Vista when Xenta Server is connected.

Environment

TAC Vista

TAC Xenta Server

Cause

If you add a stand alone Xenta Server on a Lon network it will send out heartbeats just like TAC Vista does.

So the affect will be the same as having 2 TAC Vista servers on the same network.  But there is a way to turn this off.

In Xbuilder you can turn this off by setting "Alarm Server" to disabled

Resolution

  1. In Xbuilder click on the LON object
  2. Under General properties change "Alarm Server" to disabled.
  3. Download the project.