Issue

ZBuilder will not open on certain commissioned Xenta 121s in Lonmaker. It will open on others in the same network.

Environment

  • ZBuilder
  • LonMaker

Cause

Incorrect or corrupted configuration parameters prevent the ZBuilder plug-in from opening on specific Xenta 121s.

Resolution

  1. Right-click on the device in LonMaker and choose Browse
  2. Take a screen capture of the various settings that will need to be re-entered
  3. Re-commission the Xenta 121 controller with default values (this will erase any configurations that have been made)
  4. ZBuilder will now work correctly.
  5. Re-enter any previously configured parameters