Issue

Even though "Clear when enabled" is configured on a trend log, the trend data is not cleared.

Environment

Enterprise Server

Automation Server

Trend Logs

Cause

The property "Clear when enabled" only affects the trend data when the trend log is goes from disabled to enabled.

This is not the same as the activation method of the trend log. Activation method changes the Status from Stopped to Started etc.

Resolution

Select the Trend log, right-click on it and select Activation, then select "Disable trend log".

Select the Trend log, right-click on it and select Activation, then select "Enable trend log".

 